Section 440.4(B) of the 2005 NEC requires that the Short Circuit Current Rating (SCCR) be included on a visible nameplate for "Hermetic Refrigerant Equipment" having multiple motors or combination loads, when supplied by an OCPD of more than 60A .

A major industrial HVAC equipment manufacturer states that their equipment is excluded from this requirement (even in states that have adopted the 2005 NEC) because it is "Listed" per UL 1995 and that is the only thing that they must comply with. They state that this NEC requirement only applies to equipment that is "built up" in the field.


Is the manufacturer's position correct?


(FYI: although this UL standard requires that some basic electrical information be included on the nameplate, it does not require that the SCCR be determined, nor does it require that the SCCR be provided on any nameplates).
 
Replies continue below

Recommended for you

In the "old days" the manufacturer would be correct. But the line is not as clear as it once was. The NEC has definitely crossed the boundary into factory assembled equipment now. Unfortunately for you, that means that it is going to be up the the interpretation of the local AHJ, and their word is (relatively) final. If they choose to require compliance with that section of the NEC, the manufacturer can argue all day and still get rejected.
 
I wouldn't think so. The UL label is necessary for NEC compliance, but(in general)it does not trump NEC requirements.

I agree with jraef - it's going to be up to the AHJ.



 