UL508 Disconnect vs UL98 Disconnect

Status
Not open for further replies.

rpm3232

Electrical
Dec 29, 2009
1
When is it OK to use a UL508 Disconnect in place of a UL98 disconnect on a UL508A listed panel? We have a panel that mainly controls a motor, but has other circuits (ie. PLC, I/O). This must go through UL certification soon. I have heard multiple explanations on this and could use a NEC 409 reference or UL508A. The panel, nor the equipment it controls, is not classified as "Industrial Machinery".
 
Replies continue below

Recommended for you

If your switch is required to be suitable as a motor disconnect or manual motor controller, it needs to be marked as such -- and UL 508 applies. (UL 508A 30.1.5 and table SA-1).

If not required to be suitable as a motor disconnect or manual motor controller, it can be UL 98. (UL 508A 30.1.4 and table SA-1).

Those are my opinions; the opinions of your UL field inspector may vary. Best suggestion: ask him.