unbalance voltage

Status
Not open for further replies.

wuqn

Electrical
Dec 2, 2005
26
hi
when generator run, measured voltages : Vab= 417, Vbc=420, Vca= 392.
Vca is much lower than the others. what's the problem ? how can i fix it? thanks
 
Replies continue below

Recommended for you

It sounds like unbalanced loads.
yours
 
3 phases. run unload
 
If the stator is delta connected, maybe an interturn fault could be considered.
Is it possible to measure the winding resistance between terminals?
 
Hi wuqn;
What size is the generator?
Is it delta or wye?
If it is wye, is the center point grounded?
Have you tried putting a load on it?
yours
 
the stator is wye. the center point is grounded.
it's ok when i put load on it. but the voltage is still unbalance. the generator is paralled with other generators.
may be the ground resistance is high ?
 
the generator is 550kVA.
 
Sounds like a winding fault or connection problem. Should check internal resistances and possibly do a insulation resistance test and a polarization index test.
 
What's OK when you put a load on it? Are the voltages normal or not when the generator is loaded? If so, you don't have a problem.
 