Lionel said:
The only thing that really matters is the current imbalance in conjunction with the motor load.
If that is response to me, I believe you're missing my point. It depends what's causing the current unbalance. If you have a high resistance connection inside the motor, that connection can overheat and burn open, irrespective of the level of current unbalance and the motor's ability to withstand that current unbalance.
Let's say we postulate a high-resistance internal connection right where the T-leads attach to the winding. It is effectively in series with the winding, indistinguishably electrically from an external high resistance connection. You guys aren't saying that this scenario would always lead to motor failing by thermal effects from the resulting current unbalance before the connection burns open... are you? Because if you are saying that, then I'll show you a high-resistance motor lug that burned open during service on a motor that was healthy both before and afterwards, and I'll ask you why the motor winding didn't go first (why didn't the motor winding act like a fuse to protect the lug!).
I have great respect for both of you guys... Lionel the long-time eng-tips power guru and Gr8blu the new guy here who already has given a lot of great input on this forum (I've learned some things). I think we're just looking at it in different ways....
You're asking what amount of resistive unbalance will cause a current unbalance that the motor cannot tolerate. Sure that's a question we can ask but it's not the only question. Another key question we can ask is what's causing that resistive unbalance (some causes are more concern than others). But we don't know the answer to what's causing it without inspecting it closer, so we fall back on a related but easier-to-answer question "
is this resistance imbalance within normal variability for this type of motor". If it's within normal variability we can attribute it to normal manufacturing variations (T-lead lengths differences, endwinding pole jumper configurations, coil endwinding length variations, maybe
minor internal connection resistance variations, measurement accuracy), but if its outside of normal variability then we have to consider other explanations (high resistance connection, or maybe coil miswiring). We can see the evidence of that approach in the EPRI document that I quoted 13 Sep 21 14:13... they have higher resistance unbalance limit for concentric wound motors than for lap wound wound motors. What is the basis for that difference? It's NOT because concentric wound motors can tolerate thermal effects from current unbalance due to resistive imbalance better! It's because the endwinding geometry of concentric windings can create an additional phase resistive unbalance higher than lap wound motors. In other words they're using the approach of checking whether the measurement falls outside the range of at normal variability. And if it falls outside the range of normal variability, then it raises the question of something unusual going on inside the motor like possibly a high resistance internal connection.
So to recap, the standard approach used by the EPRI specification quoted above for evaluating resistive unbalances in induction motors is NOT based on the resulting current unbalance and the motor's ability to tolerate it.... It's based on deviation from normal expected variability.
Again there are lots of ways to look at it. Maybe you don't think postulating a particular condition like high resistance connection inside the motor is fair.... I wouldn't necessarily disagree, I'd say that's a whole 'nother discussion to be had. As we all know it depends upon the criticality of the motor, the history of the motor (was it just rewound, do we trust those rewinders, how long has the motor survived already with this resistive unbalance, is the unbalance trending up, etc)...
=====================================
(2B)+(2B)' ?