this is not my area of expertise? but i was asked the question and i am now curious.
There are 3 small reactors. Each one is a standalone ultra violet lamp operating at 2000V - fed via a 400/3500V transformer. Each lamp is rated at 27kW (not important) One. two or three lamps may be on together -
each is fed from its own panel and transformer. Each panel has a separate 3-phase supply from an MCC.
Each transformer primary takes 107A at 400V connected across two phases.
This brings us to the question:
Say lamp 1 is connected across phases L1 and L2
and lamp 2 is connected across phases L2 and L3
When two lamps are on, phase L2 is carring a bigger load but what isthat load?
The loads are not balanced 3-phase loads so it will not be 2 x 107A
I think we have to go back to bacics and consider phase angles and sine waves, etc. to work it out. But I have forgotten all that.
Because the lamp is across 2 phases, we are looking at line voltage 400V and line current 107A - not phase values. It makes sense if you sketch out the star of the phase vectors at 120 degrees and show 2 lamps connected.
Voltage is ok
V line = V phase x square root of 3 (1.732)
i.e. 400 = 230 x 1.732
But I have forgoten how to convert line current to phase current.
I reckon phase current is approx 2/3 of 2 x 107A = 142A
It is probably a factor like 1.732 divided by 3
Connecting 3 lamps will be the same as for 2 lamps - except all phases will then be balanced.
Would you know how to calculate the phase current? Or know anyone who knows? Have you ever dealt with anything like this?
There are 3 small reactors. Each one is a standalone ultra violet lamp operating at 2000V - fed via a 400/3500V transformer. Each lamp is rated at 27kW (not important) One. two or three lamps may be on together -
each is fed from its own panel and transformer. Each panel has a separate 3-phase supply from an MCC.
Each transformer primary takes 107A at 400V connected across two phases.
This brings us to the question:
Say lamp 1 is connected across phases L1 and L2
and lamp 2 is connected across phases L2 and L3
When two lamps are on, phase L2 is carring a bigger load but what isthat load?
The loads are not balanced 3-phase loads so it will not be 2 x 107A
I think we have to go back to bacics and consider phase angles and sine waves, etc. to work it out. But I have forgotten all that.
Because the lamp is across 2 phases, we are looking at line voltage 400V and line current 107A - not phase values. It makes sense if you sketch out the star of the phase vectors at 120 degrees and show 2 lamps connected.
Voltage is ok
V line = V phase x square root of 3 (1.732)
i.e. 400 = 230 x 1.732
But I have forgoten how to convert line current to phase current.
I reckon phase current is approx 2/3 of 2 x 107A = 142A
It is probably a factor like 1.732 divided by 3
Connecting 3 lamps will be the same as for 2 lamps - except all phases will then be balanced.
Would you know how to calculate the phase current? Or know anyone who knows? Have you ever dealt with anything like this?