yoleven
Civil/Environmental
- Dec 4, 2009
- 2
Hi.
I need to replace an air conditioning unit for an MCC room. Currently there is a 10 ton unit and it cools sufficiently. The fins are corroding, etc.
I have calculated the area of the room at approx. 23 ft2
I have transformers with the following kVA rating..
45, 1250, 1250, 15, 50, 30, 45, 1250, 1250, 150.
The heat output for no load on the transformers I got from a table at 14000 watts.
I guessed the change in temp. to be 20 deg. F.
Using the equation:
(watts * 3.413) + (1.25 * 23ft2 * 20deg F) = 48357 Btu/hr
48357/12000 = 4 tons of cooling.
If I do the same calculation with a heat loss with a 50% load I get 13 tons of cooling.
What am I doing wrong. This doesn't seem correct because a 10 ton unit is keeping the room cool.
Thank you