reviest54
Structural
- Apr 22, 2016
- 21
Hello all
Our firm designed a 3 story structure with fully grouted CMU bearing/shear walls. The mason did his grouting in high lifts 8-12 feet with 100% cleanouts according to the inspection reports. No issues were reported in the inspection reports.
After several mistakes the mason was fired after completing the second story, and a new mason was hired. The first thing the new mason did was check the previous work and he found several hollow blocks throughout the structure.
Here is the only repair I can see:
1. Prism tests of wall to see what the strength of the "well constructed" portions is.
2. Locate all of the unconsolidated grout locations (non-destructive and/or destructive testing).
3. Demo a sufficient distance beyond each unconsolidated area to provide new fully developed reinforcing that is epoxied into acceptable CMU.
4. Infill with CMU or concrete depending on the extent.
Does anyone have a more clever approach or see an issue with mine?
Thanks.
Our firm designed a 3 story structure with fully grouted CMU bearing/shear walls. The mason did his grouting in high lifts 8-12 feet with 100% cleanouts according to the inspection reports. No issues were reported in the inspection reports.
After several mistakes the mason was fired after completing the second story, and a new mason was hired. The first thing the new mason did was check the previous work and he found several hollow blocks throughout the structure.
Here is the only repair I can see:
1. Prism tests of wall to see what the strength of the "well constructed" portions is.
2. Locate all of the unconsolidated grout locations (non-destructive and/or destructive testing).
3. Demo a sufficient distance beyond each unconsolidated area to provide new fully developed reinforcing that is epoxied into acceptable CMU.
4. Infill with CMU or concrete depending on the extent.
Does anyone have a more clever approach or see an issue with mine?
Thanks.