TWD82
Electrical
- Oct 4, 2005
- 10
I've been reading this forum since I got out of school (about a year ago). I've learned alot from everyone here, hopefully I can start contributing as I become more competent in the power field, for now I have a question I would like advice on. Recently we had a main breaker trip on underfrequency (load shedding scheme) during an arcing feeder fault (before the feeder breaker could trip on time-overcurrent). The event report showed the frequency dropped to 58.5 Hz, so somehow the arcing fault "tricked" the relay into thinking the frequency had dropped. Is this caused by harmonics generated in the arcing fault? Would moving the PT inputs from the low side of the transformer (grounded wye) to the high side (delta) smooth out the waveform somehow and help the relay from being tricked again? The relay is an SEL 351.