Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Undercurrent Protection In 5th Harmonic Filter

Status
Not open for further replies.

Keegan Howe

Electrical
May 24, 2017
2
Is anyone able to explain the purpose of undercurrent protection in a 5th harmonic filter.

With reference with the attached schematic, why are the highlighted CTs installed in the resistance circuit of the filter and why would a low current in this circuit cause a fault condition? Is it just to ensure that the resistors have not opened circuited?
Undercurrent_Protection_pypzcg.png
 
Replies continue below

Recommended for you

In my view an alarm should be good enough for the resistor open condition. This is a damping resistor to absorb the surges. So monitoring the availability of these resistors is very crucial. But it need not trip immediately. The filter can be shut down manually.

Again, ff the installation is un-attended, better trip rather than going unattended!
 