underground cable impedance data

Status
Not open for further replies.

SphincterBoy

Electrical
Aug 29, 2001
124
Does anyone know of a source of positive and zero sequence impedance data for various sizes of high voltage underground cables? Ex: 4/o aluminum, 15kV, concentric neutral, 220-mil
EPR insulation

The websites for Okonite, Kerite, etc. have very minimal data for this, and do not list any of the impedance data.
 
Replies continue below

Recommended for you

can any body tell how to calculate voltage drop if there are more than one condutors per phase. if the connection is in between a transformer and low voltage switchgear. what are the considerations?
 
You have to calculated this way 1/Rt=1/R1+1/R2, and same deal for the inductance.
 