IBRCAN
Electrical
- Feb 3, 2012
- 53
I am a technician in the on-site power generation industry. I do a lot of work in quarries, and every now and then I run into a crusher motor starting issue.
I understand that, as with any electrical installation, feeder cables from the generator to the mcc should be kept as short as possible to reduce the effects of voltage drop. One of my co-workers in particular is adamant that cables should never be coiled to prevent voltage drop.
Am trying to understand and quantify the effects of the feeder cables being coiled. Obviously the coils cause undesirable heat build-up for one thing. The coils will introduce a small amount of inductive reactance into the circuit as well.
Case in point--200 hp, soft started jaw crusher motor, 320 kw prime rated diesel generator with PMG. This generator had been used to start the same and similar sized loads before. During start up of the crusher, soft start was faulting on under voltage. I connected power analyzers at both the generator and soft start. There appears to be at least 100 V lost between the generator and soft start during motor start-up, with in rush current of approx. 700 A at 600 V. Distance between generator connection box and mcc was probably 25', however there is over 100' of 4/0 copper cable run per phase, with the excess coiled up and hung on the side of the generator trailer. There were perhaps 10 coils per phase, 3 ft in diameter. Calculated voltage drop using cable diameter and length indicates a negligible voltage drop, only a few volts. I also calculated the inductance of the coils, which seems to be in microhenries and would not cause significant losses.
I know there are a lot of other variables at play when it comes to generator/motor starting, but I am looking for guidance as to the effects of coiled cable in particular. Thanks.
PS, The generator AVR was equipped with a line loss compensation mode, which I enabled and seems to have solved the motor starting issue.
I understand that, as with any electrical installation, feeder cables from the generator to the mcc should be kept as short as possible to reduce the effects of voltage drop. One of my co-workers in particular is adamant that cables should never be coiled to prevent voltage drop.
Am trying to understand and quantify the effects of the feeder cables being coiled. Obviously the coils cause undesirable heat build-up for one thing. The coils will introduce a small amount of inductive reactance into the circuit as well.
Case in point--200 hp, soft started jaw crusher motor, 320 kw prime rated diesel generator with PMG. This generator had been used to start the same and similar sized loads before. During start up of the crusher, soft start was faulting on under voltage. I connected power analyzers at both the generator and soft start. There appears to be at least 100 V lost between the generator and soft start during motor start-up, with in rush current of approx. 700 A at 600 V. Distance between generator connection box and mcc was probably 25', however there is over 100' of 4/0 copper cable run per phase, with the excess coiled up and hung on the side of the generator trailer. There were perhaps 10 coils per phase, 3 ft in diameter. Calculated voltage drop using cable diameter and length indicates a negligible voltage drop, only a few volts. I also calculated the inductance of the coils, which seems to be in microhenries and would not cause significant losses.
I know there are a lot of other variables at play when it comes to generator/motor starting, but I am looking for guidance as to the effects of coiled cable in particular. Thanks.
PS, The generator AVR was equipped with a line loss compensation mode, which I enabled and seems to have solved the motor starting issue.