MIER said:
Sorry guys,
It is 6 poles and 930 rpm - so I guess the effency is "low" due to a slow engine.
We am trying to size a UPS towards worst case - and even though full load is the best efficiency it will be still be "worst case" right?
Meaning: 400 x 6 x 1.73 = 4.15kVA.
4.15k x 0.83 = 3.44 kW
Just an info; it will be started up by a soft starter limited to 6.0 A.
Several flaws in the concept here.
As Bill pointed out, limiting the starting current to 100% of FLC will result in a stall and an unsuccessful application. A soft starter can only limit current by limiting voltage, which limits torque. To attain a Current Limit at 100% of FLC when it wants to be 200% of FLC (the minimum required for even the lightest of loads) the soft starter will have to phase back the voltage to approximately 50% of RMS, so the torque will be approx. 25% of BDT, which would have been maybe 220% of FLT, so you will have roughly only 55% of FLT at the motor shaft at 100% Current Limit. I have never seen that work. Typical Current Limit for something easy like a pump or fan is 250-300% FLC, anything heavy may be 350-450%. In addition, Soft Starters need relatively clean power on the input so they can sense when to fire the SCRs. If the output of your UPS is PWM, chances are the Soft Starter will not work properly anyway.
Aside from that, your math is flawed as well. 2.2kW is 2.2kW, it doesn't matter how you get there. But in a motor, that 2.2kW rating is the MECHANICAL output of the motor, not the electrical input. The electrical input is the output (2.2kW) divided by the efficiency, which you do not know. But ASSuming (from the other posts) a 71% eff, the the electrical input would be 2.2kW/.71 = 3.1kW. But that would ONLY be for running load capability. Assuming the Soft Starter will not work (as I said above), your choices are DOL or VFD.
A VFD would be OK with PWM on the input because all it is doing is converting back into DC anyway, and because it controls frequency AND voltage, you will likely be able to start that motor with 3.1kW from the UPS, as long as starting time is irrelevant to you.
If you go with a DOL start, you will likely need a UPS that is capable of 18kW because unlike other power sources, a UPS is typically not built with any "reserve capacity" in the design. They are generally NOT intended to be used on induction motors.
The only other viable reduced voltage starting method for you would be an Autotransformer starter, but nobody makes one that small, you would have to roll your own from scratch.
Do NOT, I repeat, NOT attempt to use Star-Delta on this, the result will be a dead UPS and/or motor.