I've been doing some reading on water hammer and trying to 'really' understand it.
I've been asked to look at a relatively simple problem of a pump station pump water up a relatively constant slope. Initially this was to be done by others, but I was keen (stupid) to learn.
Details:
Flow: 50 MLD
Head: ~250 m (~200m static)
Length: 10,000m
Diameter: ~1000mm
Pipe: Steel, ~10mm thick
I've assumed the most likely cause of water hammer will be due to pump trip as; pump isolation valves are manual, there is a control valve near discharge, but this is relatively 'slow' (over 60s open/close). At this stage I've assumed pump will take less than 5s before it's head drops below static head, hence flow 'stops'.
I've assumed time for 'valve closure' (in this case pump stop) is 5s, therefore given celerity is in the order of 1100 m/s, this disturbance is rapid (5s < 2L/a < 20). Therefore elastic theory should used.
Elastic theory indicates that I'll get a pressure rise of about 100m.
I have two question:
1. Does a pressure rise of 100m seem to be accurate based on my simple analysis? When the pump stops, the water column continues to move, causing a low pressure at the pump discharge. This low pressure wave travels up the water column. The low pressure cause the water column to stop, then it will 'pull' the water back, at which point it will collide with the check valve and cause a pressure spike. Should I assume that if the spike is 100m, the low pressure will be -100m (if static head 200m, then 100m)?
2. It has been suggested that a fast acting non return valve can reduce the pressure spike. Is this true and if so how? Or does it just protect the pump?
I've been asked to look at a relatively simple problem of a pump station pump water up a relatively constant slope. Initially this was to be done by others, but I was keen (stupid) to learn.
Details:
Flow: 50 MLD
Head: ~250 m (~200m static)
Length: 10,000m
Diameter: ~1000mm
Pipe: Steel, ~10mm thick
I've assumed the most likely cause of water hammer will be due to pump trip as; pump isolation valves are manual, there is a control valve near discharge, but this is relatively 'slow' (over 60s open/close). At this stage I've assumed pump will take less than 5s before it's head drops below static head, hence flow 'stops'.
I've assumed time for 'valve closure' (in this case pump stop) is 5s, therefore given celerity is in the order of 1100 m/s, this disturbance is rapid (5s < 2L/a < 20). Therefore elastic theory should used.
Elastic theory indicates that I'll get a pressure rise of about 100m.
I have two question:
1. Does a pressure rise of 100m seem to be accurate based on my simple analysis? When the pump stops, the water column continues to move, causing a low pressure at the pump discharge. This low pressure wave travels up the water column. The low pressure cause the water column to stop, then it will 'pull' the water back, at which point it will collide with the check valve and cause a pressure spike. Should I assume that if the spike is 100m, the low pressure will be -100m (if static head 200m, then 100m)?
2. It has been suggested that a fast acting non return valve can reduce the pressure spike. Is this true and if so how? Or does it just protect the pump?