Oblsss
Electrical
- Nov 7, 2013
- 42
Dear sirs,
I am currently working on a case of connecting an island (300 m from the coast) with the LV distribution system.
Two (for redudancy reasons) 3-core PILC/SWA lead sheathed cables will depart from the secondary of a distribution transformer (wye connection with the common point grounded)to travel the underwater section of the connection before transitioning to a three-core waveform (copper concentric conductor) cable in the island side.
The loading of the circuit is expected to be assymetrical, therefore the neutral of the system will be lightly loaded.
11kV-PILC-Cable
Waveform-Cables-3-Core
My main concern is the following:
1. At the transition joint, corrosion is expected due to the dissimilar metals of the metal shields, ie copper on one side with lead + steel on the other. The presence of moisture, or in the worst case contact with sea water in combination with the continuous loading of the shield due to the asymmetry of the phases can only speed up the corrosion process.
In case of heavy corrosion there is a risk of an open neutral condition on the island side.
My thought is to lay an extra 1-core cable to act as a neutral, ie connected from the neutral point of the distribution transformer's secondary to the copper concentric conductor of the three-core waveform cable in the island side.
The lead sheath + steel armour of the three-core PILC/SWA lead sheathed cables will be grounded on one point only with the other end insulated from ground and will only serve as a fault current path in case of single phase fault to ground.
Am i missing something here?
Thank you in advance,
George
I am currently working on a case of connecting an island (300 m from the coast) with the LV distribution system.
Two (for redudancy reasons) 3-core PILC/SWA lead sheathed cables will depart from the secondary of a distribution transformer (wye connection with the common point grounded)to travel the underwater section of the connection before transitioning to a three-core waveform (copper concentric conductor) cable in the island side.
The loading of the circuit is expected to be assymetrical, therefore the neutral of the system will be lightly loaded.
11kV-PILC-Cable
Waveform-Cables-3-Core
My main concern is the following:
1. At the transition joint, corrosion is expected due to the dissimilar metals of the metal shields, ie copper on one side with lead + steel on the other. The presence of moisture, or in the worst case contact with sea water in combination with the continuous loading of the shield due to the asymmetry of the phases can only speed up the corrosion process.
In case of heavy corrosion there is a risk of an open neutral condition on the island side.
My thought is to lay an extra 1-core cable to act as a neutral, ie connected from the neutral point of the distribution transformer's secondary to the copper concentric conductor of the three-core waveform cable in the island side.
The lead sheath + steel armour of the three-core PILC/SWA lead sheathed cables will be grounded on one point only with the other end insulated from ground and will only serve as a fault current path in case of single phase fault to ground.
Am i missing something here?
Thank you in advance,
George