rockman7892
Electrical
- Apr 7, 2008
- 1,161
I was recently asked to look into momentary power outages at a facility that has been experiencing re-occurring momentary outages that is causing motors to drop out and electronics to reset.
This facility is served at 4.16kV from the local utility through a M-T-M 4.16k Switchgear lineup. We recently connected a meter to the secondary metering equipment (Pt's and CT's) at the 4.16kV Switchgear main in order to try to capture one of these momentary outages. (Other main is open with Tie Breaker Closed. During these outages no relays pickup nor do any breakers trip.
We were able to successfully capture one of these momentary outages and found that the voltage drops all the way to 0V for a duration of approximately 600ms before it is restored back to 4.16kV. Approximately another 566ms later the voltage drops close to 0V again this time for a shorter duration of only 92ms. This was the only event we were able to capture during the monitoring period.
I've included an attachment that shows the voltage and current trends during this event. The first two trends show the voltage and current respectively and the third trend shows the voltage and current of one phase on the same trend. Looking at these trends it appears that immediately after the voltage starts to decay the load current quickly increases. This is likely to be expected with motor loads which it mostly what this facility consists of (chiller loads etc..)
Any ideas on what may be causing these momentary outages. It would appear that it has to be something happening on the utility end? Could this perhaps be a re-closer or some other automatic protective device on the utility side opening and then re-closing quickly?
This facility is served at 4.16kV from the local utility through a M-T-M 4.16k Switchgear lineup. We recently connected a meter to the secondary metering equipment (Pt's and CT's) at the 4.16kV Switchgear main in order to try to capture one of these momentary outages. (Other main is open with Tie Breaker Closed. During these outages no relays pickup nor do any breakers trip.
We were able to successfully capture one of these momentary outages and found that the voltage drops all the way to 0V for a duration of approximately 600ms before it is restored back to 4.16kV. Approximately another 566ms later the voltage drops close to 0V again this time for a shorter duration of only 92ms. This was the only event we were able to capture during the monitoring period.
I've included an attachment that shows the voltage and current trends during this event. The first two trends show the voltage and current respectively and the third trend shows the voltage and current of one phase on the same trend. Looking at these trends it appears that immediately after the voltage starts to decay the load current quickly increases. This is likely to be expected with motor loads which it mostly what this facility consists of (chiller loads etc..)
Any ideas on what may be causing these momentary outages. It would appear that it has to be something happening on the utility end? Could this perhaps be a re-closer or some other automatic protective device on the utility side opening and then re-closing quickly?