Power0020
Electrical
- Jun 11, 2014
- 303
While reviewing a 220/66 kV substation design in IEC world, I noticed that the power transformer has two neutral points connected to ground through disconnectors, I learnt that these DS are normally closed during operation and opened only for maintenance.
The 220 kV neutral side is equipped with 123 kV surge arrester, disconnector and current transformer. 36 kV rated similar equipment is used for 66 kV neutral side.
Some points I noticed here need to understand:
1- Why, ever, should the neural point be opened? what maintenance requires that?.
2- If, once the DS is open, a fault occurs somewhere on 220 kV network, the faulted phase to ground will cause the "float" neutral voltage to rise up, while the two other phases are still connected to some other transformers having their neutrals solidly grounded, heavy circulating current will appear on these healthy phases!, again, the neutral point voltage with respect to ground will be almost the phase voltage, i.e. 220 kV rated equipment should be placed, not 123 kV "L-L". The same for 66 kV side.
In other words, the neutral to ground voltage will be 220/1.732 = 127 kV, the proposed DS has a phase-to-phase insulation"though it is made of single of 123 kV i.e.71 kV phase-to-ground insulation!.
I tried to calculate the surge arrestor TOV capability, it is still lower that the tripping time of 1 S in that case and an explosion may well occur!, if no flashing takes place.
3- Why the CT isn't placed after the disconnector to reduce the required insulation voltage? the CT will never read a surge current "lightning, maybe" going through the surge arrestor when the DS is left open "the healthy case with no faults".
4- The Transformer neutral bushing is clearly rated at 123 kV "graded insulation" as well for 220 kV side and 36 kV for 66 kV side, I wonder if this permits running it open, ever! any IEC or IEEE recommendations for that?
The 220 kV neutral side is equipped with 123 kV surge arrester, disconnector and current transformer. 36 kV rated similar equipment is used for 66 kV neutral side.
Some points I noticed here need to understand:
1- Why, ever, should the neural point be opened? what maintenance requires that?.
2- If, once the DS is open, a fault occurs somewhere on 220 kV network, the faulted phase to ground will cause the "float" neutral voltage to rise up, while the two other phases are still connected to some other transformers having their neutrals solidly grounded, heavy circulating current will appear on these healthy phases!, again, the neutral point voltage with respect to ground will be almost the phase voltage, i.e. 220 kV rated equipment should be placed, not 123 kV "L-L". The same for 66 kV side.
In other words, the neutral to ground voltage will be 220/1.732 = 127 kV, the proposed DS has a phase-to-phase insulation"though it is made of single of 123 kV i.e.71 kV phase-to-ground insulation!.
I tried to calculate the surge arrestor TOV capability, it is still lower that the tripping time of 1 S in that case and an explosion may well occur!, if no flashing takes place.
3- Why the CT isn't placed after the disconnector to reduce the required insulation voltage? the CT will never read a surge current "lightning, maybe" going through the surge arrestor when the DS is left open "the healthy case with no faults".
4- The Transformer neutral bushing is clearly rated at 123 kV "graded insulation" as well for 220 kV side and 36 kV for 66 kV side, I wonder if this permits running it open, ever! any IEC or IEEE recommendations for that?