jktwn
Electrical
- Jun 12, 2001
- 47
We recently had a GE 600HP DC motor suffer overheating and destruction when the cooling air intake became blocked by debris. During the the investigation it was discovered that the motor overtemperature devices (thermistor - GE p/n 36A172828BBG01) were not configured to work with the Siemens drive. This goes back to when the line was installed.
Our problem is that GE will not divulge thermistor information that would allow us to correctly program the Siemens drive. The only information they will provide is that the "Trip Temperature" is 140/130 C. Has anyone else had problems with GE getting the information you need and has anyone found a solution. We have to get the OT working and really don't want to redesign.
thanks,
Wayne
Our problem is that GE will not divulge thermistor information that would allow us to correctly program the Siemens drive. The only information they will provide is that the "Trip Temperature" is 140/130 C. Has anyone else had problems with GE getting the information you need and has anyone found a solution. We have to get the OT working and really don't want to redesign.
thanks,
Wayne