SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
IBC
I am being told the minimum separation distance between two buildings is 31' but I don't see how this is arrived at given the following:
Buildings are manufactured steel type with 8" bent metal purlins, rigid metal frames and insulated metal roof decks. Eave heights are 24'-0" with peaks at 33'-4 1/2". Steel is not protected.... pretty much your standard bent metal purlin buildings.
Buildings are all sprinkled using ESFR systems. k=16.8 pendent discharging at 52 psi. Obviously buildings are used for storage of a wide variety of Class I through Class IV commodities and even some non-expanded plastics.
All the buildings are owned by a single owner who leases out the complex to a variety of different renters.
I can understand separation distances between buildings having different owners but on a single property?
As I am not the building professional I don't need to be able to answer this but I would like to know just for myself.
I am being told the minimum separation distance between two buildings is 31' but I don't see how this is arrived at given the following:
Buildings are manufactured steel type with 8" bent metal purlins, rigid metal frames and insulated metal roof decks. Eave heights are 24'-0" with peaks at 33'-4 1/2". Steel is not protected.... pretty much your standard bent metal purlin buildings.
Buildings are all sprinkled using ESFR systems. k=16.8 pendent discharging at 52 psi. Obviously buildings are used for storage of a wide variety of Class I through Class IV commodities and even some non-expanded plastics.
All the buildings are owned by a single owner who leases out the complex to a variety of different renters.
I can understand separation distances between buildings having different owners but on a single property?
As I am not the building professional I don't need to be able to answer this but I would like to know just for myself.