I have a temporary situation where a concrete plug has to be cast into a caisson below the water table under tremie conditions. The water then gets pumped out resulting in a head of approx 4m between the invert of the caisson and the surrounding water table. (the final situation sees a seond reinforced concrete slab cast on top of the tremied concrete.
The caisson is 4.7meter by 5.5 meter and the tremied plug will be 500mm thick.
Would it be unreasonable to treat the unreinforced tremied concrete as a bending element and to accept that the concrete will respond safely in an elastic manner to the bending loads.
Based on the "slab" operating as a 2-way spanning slab, the tensile bending stress would be approx 6% of the concrete compressibe strength.
Thanks for responses
Alten