Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Unreinforced Slab on Grade Small Overturning Moment Checks

Status
Not open for further replies.

mountaineers19

Structural
Jun 4, 2024
5
0
0
US
I am more of a steel guy but I am starting to get into some concrete stuff so I wanted to get some guidance on the proper checks for unreinforced slabs subjected to light moment loads from a steel column. I know I need to check punching shear, concrete breakout strength of a single anchor and of the bolt group and compare that to the tension developed by the over turning moment. But as besides that what other checks do I need to perform. I know most people will say a footer is needed but the loads I am talking about are around 2-3 kip-ft on 8" fiber reinforced slabs.
 
Replies continue below

Recommended for you

You need to check flexure. ACI 318 has a chapter which deals with plain concrete, and the nominal moment capacity (and punching shear capacity for that matter) are quite a bit lower than what is allowed for reinforced concrete. The axial load from your column will cause bending moment in the slab in two directions, similar to a spread footing.

DaveAtkins
 
Status
Not open for further replies.
Back
Top