So how do so many engineers design a basement retaining wall with a footing at the base that is barely wider than the wall, and claim "the loads balance out"?
The footing below a 9 foot retaining wall is 20 inches wide, 12 inches thick. It has no overturning resistance and is clearly designed to act as a pin-pin model.
A few questions (asking for a friend):
1. how does a 1/2" diameter anchor bolt at 4 to 6 (!!) ft in a 2x plate on center support a top of wall reaction of nearly 450 plf. The bolt has 1/4 to 3/8 of gap because they drill it with a 1 inch bit so they can slide the sill plate over the bolts easier. Do not say friction.
2. when you have a walkout basement, and one of your walls clearly does not 'balance' against an opposite opposing side of the house, then what? Do not say "we pick it up in internal framing" or "the J bolts pick up everything".
3. if you pour your slab perimeter with a 1/2 inch expansion gap (ACI says don't pour them tight) how exactly does that slab at the base form a reaction against your wall? It is air. Does air transfer load?
4. how do you transfer 450 plf into a floor in a condition where the floor joists are parallel to the wall. I have seen the plans. There is no blocking between joists.
I see really smart people doing this (I see your plans come across my desk once in a great while), and am just wondering, what am I missing? Were you born before the age of physics, or perhaps in a world where gravity and fluid pressure do not actually exist? Are your contractors magically buying sill plates with the anchor bolts literally 'grown' with the tree the board was cut from? If so, please teach me your magical ways.
The footing below a 9 foot retaining wall is 20 inches wide, 12 inches thick. It has no overturning resistance and is clearly designed to act as a pin-pin model.
A few questions (asking for a friend):
1. how does a 1/2" diameter anchor bolt at 4 to 6 (!!) ft in a 2x plate on center support a top of wall reaction of nearly 450 plf. The bolt has 1/4 to 3/8 of gap because they drill it with a 1 inch bit so they can slide the sill plate over the bolts easier. Do not say friction.
2. when you have a walkout basement, and one of your walls clearly does not 'balance' against an opposite opposing side of the house, then what? Do not say "we pick it up in internal framing" or "the J bolts pick up everything".
3. if you pour your slab perimeter with a 1/2 inch expansion gap (ACI says don't pour them tight) how exactly does that slab at the base form a reaction against your wall? It is air. Does air transfer load?
4. how do you transfer 450 plf into a floor in a condition where the floor joists are parallel to the wall. I have seen the plans. There is no blocking between joists.
I see really smart people doing this (I see your plans come across my desk once in a great while), and am just wondering, what am I missing? Were you born before the age of physics, or perhaps in a world where gravity and fluid pressure do not actually exist? Are your contractors magically buying sill plates with the anchor bolts literally 'grown' with the tree the board was cut from? If so, please teach me your magical ways.