Laplacian
Electrical
- Jul 15, 2002
- 246
We have an application with an 81KW heater bank controlled by a 480V 3-phase SCR controller. Each heater probe is 240V, 750W, 1-phase. The probes are connected in series-delta; 2 probes in series per delta leg, 18 parallel legs for 108 total probes.
We are experiencing several failure modes with these heaters. It is not feasible to change probe type or voltage at this point; 81KW is absolutely required.
Fuses blow frequently; each leg of each delta is fused. One fuse removes 50% of the KW from the respective delta leg. I am seeking to fuse each probe independently for both ease in troubleshooting and process reliability.
My idea was to install a step down transformer at the heater location to 240V l-l versus the existing 480V l-l so all probes can be paralleled and fused independently. I wanted to go with a delta-wye transformation as there are no delta-delta transformers in our plant (the mere thought would bring grievances from the electricians).
I began searching for a multi-tapped 3-phase transformer to no avail. I then searched for single phase multi-tapped transformers to connect in a bank. I need 139V l-g on the wye side to get my nominal 240V l-l heater probe voltage. The best I could find was a Sola transformer that would deliver 133V @ 480V input.
Is it possible to get a custom transformer to yield 480V delta - 139V wye? I'm used to dealing with oil filled transformer manufacturers, not small dry types. Any custom dry type manufacturers out there?
We are experiencing several failure modes with these heaters. It is not feasible to change probe type or voltage at this point; 81KW is absolutely required.
Fuses blow frequently; each leg of each delta is fused. One fuse removes 50% of the KW from the respective delta leg. I am seeking to fuse each probe independently for both ease in troubleshooting and process reliability.
My idea was to install a step down transformer at the heater location to 240V l-l versus the existing 480V l-l so all probes can be paralleled and fused independently. I wanted to go with a delta-wye transformation as there are no delta-delta transformers in our plant (the mere thought would bring grievances from the electricians).
I began searching for a multi-tapped 3-phase transformer to no avail. I then searched for single phase multi-tapped transformers to connect in a bank. I need 139V l-g on the wye side to get my nominal 240V l-l heater probe voltage. The best I could find was a Sola transformer that would deliver 133V @ 480V input.
Is it possible to get a custom transformer to yield 480V delta - 139V wye? I'm used to dealing with oil filled transformer manufacturers, not small dry types. Any custom dry type manufacturers out there?