Upgrading Fire Water System

Status
Not open for further replies.

Alipooh

Chemical
Nov 18, 2013
2
I am currently working on a project to Upgrade the Existing Firewater System with a Jockey Pump. I came across a few probable alternatives to the Jockey Pump in my research. However, I would like to get an idea of the system that is used in other organization whether it’s a Jockey Pump or another technology.

Regards
 
Replies continue below

Recommended for you

What is in place currently

What is the system supplying fire hydrants only, fire sprinklers only or both or more[tt][/tt]
 
Its a refinery, the pump supplies both to hydrants and to sprinklers...currently there are two electric driven fire pumps designed at 1500 GPM at 150 psi the back up pumps are both diesel driven. There is currently no pump to maintain the pressure on the closed loop as a result the a fire water pump is constantly in operation
 
Therefore you do need a jockey pump, however, you should find the leak(s) before investing in such pump.
 