O.K. in response to my glib reply, when you throw in a non-plane-strain condition (i.e., acting on a drilled pier) a design value for passive pressure is affected by soil arching. Brinch-Hansen has a parameter called Cp that is essentially phi/10 that is used to increase the Rankine coefficient of passive earth pressure. So, for a friction angle of 30 degrees you'd calculate a Rankine Kp of 3 and then multiply that by another 3 - getting a design value of 9!!!!! Wow! How can that be? It's because the load from a horizontally-loaded drilled shaft attenuates in the X-Y plane whereas the load on a long retaining wall doesn't.
One item of note on passive pressure: Watch for strain compatibility. Just because the soil can offer an elevated amount of passive resistance, doesn't mean you want to realize that much movement for the resistance to develop.
Another item of note: DM-7 (I think it's 7.2, but it may be 7.1) has the log-spiral passive pressure charts and these are always much greater than the Rankine Kp value. There are cases where I could use more than 3, either when I'm not worried about strain compatability and I'm dealing with an open-graded aggregate (i.e., with a phi of 40 degrees or so. . .).