I have been investigating a potential power quality issue at a facility that has been losing multiple UPS devices in one of their server rooms. They were unable to tell me if these failures coincided with any particular event but they believed the issue was on the utility side due to "high harmonic distortion". Due to safety concerns and because the issue was isolated in one part of their facility, we decided to place a power quality recorder in the breaker panel for the server room. After reviewing a couple weeks of recordings, I determined that Voltage THD is just below 5% and the high levels they were referring to was the Current THD. I've placed recorders at other loads around them and I'm pretty sure that the heavily non-linear load that this panel is serving is the source of any elevated harmonics.
However, this didn't explain why they were losing a UPS every few weeks. The IT Director told me that he would discover an UPS with a failure message and there were be a flash and loud pop when he pressed the power button on the device and that this happened several times. From what I’ve been reading about the type of UPS system that they are using, the capacitors are used to correction harmonic distortion among other things. This might help explain some higher THD if the capacitors were damaged in some way. It also sounds like capacitors are more susceptible to voltage and temperature issues than any harmonic issues we’ve been observing. I have not seen any issues with the voltage that we’ve been supplying them and the server room doesn’t seem to be getting too hot when I’ve visited the facility.
It does sound like generators coordinated with UPS systems can have some issues if they are not set up properly. Most of these issues sound like they’ll simply result in the UPS switching back to battery if it doesn't like the generator output, but I found an article mentioning that the automatic transfer switch could cause some issues if there is also motor load, such as HVAC. If the transfer setting is too fast, then the paper says that it can result in damage to both the HVAC motors and UPS. The first time I visited the site for this issue, they mentioned that they just had work done on the HVAC in that room after it failed.
Does an automatic transfer switch issue sound like a reasonable path to investigate for these issues? I've attached the article that I found online regarding UPS and generator issues. I've been working on this problem for several weeks now without any good answers.
Thanks,
However, this didn't explain why they were losing a UPS every few weeks. The IT Director told me that he would discover an UPS with a failure message and there were be a flash and loud pop when he pressed the power button on the device and that this happened several times. From what I’ve been reading about the type of UPS system that they are using, the capacitors are used to correction harmonic distortion among other things. This might help explain some higher THD if the capacitors were damaged in some way. It also sounds like capacitors are more susceptible to voltage and temperature issues than any harmonic issues we’ve been observing. I have not seen any issues with the voltage that we’ve been supplying them and the server room doesn’t seem to be getting too hot when I’ve visited the facility.
It does sound like generators coordinated with UPS systems can have some issues if they are not set up properly. Most of these issues sound like they’ll simply result in the UPS switching back to battery if it doesn't like the generator output, but I found an article mentioning that the automatic transfer switch could cause some issues if there is also motor load, such as HVAC. If the transfer setting is too fast, then the paper says that it can result in damage to both the HVAC motors and UPS. The first time I visited the site for this issue, they mentioned that they just had work done on the HVAC in that room after it failed.
Does an automatic transfer switch issue sound like a reasonable path to investigate for these issues? I've attached the article that I found online regarding UPS and generator issues. I've been working on this problem for several weeks now without any good answers.
Thanks,