Mechanical
- Mar 14, 2019
- 2
We have 2 generator rated at 282kVA & 939kVA both runs automatically during power failure. But the 282kVA will be the first to supply the UPS and will be transferred to the 939kVA genset after 10-15 minutes but during the operation using the 282kVA genset an alarm appears on the UPS controller "Inverter & Mains Not Synch" and then again "Inverter & Mains Synch" several times every 1-3 minutes but it ceases when the load transferred to the bigger capacity genset. The 282kVA genset is a mechanical governor while 939kVA is electronic governor genset with ECM. We already tried to adjust the stability of the lower capacity genset (frequency varies from 59.9 to 60.3 hZ). We also adjusted the voltage same with the bigger capacity genset and also replace AVR and speed controller of the 282kVA but still couldn't cease the alarm.
Is it possible that the problem was on the UPS and not the genset? Or is the genset is to small to carry the load of the UPS? The UPS is rated at 160kVA.
Is it possible that the problem was on the UPS and not the genset? Or is the genset is to small to carry the load of the UPS? The UPS is rated at 160kVA.