Our Customer purchased a new UPS that requires the input source to be a 480VAC grounded WYE. After the new UPS was installed it was determined that the Utility source is a 480 Delta.
The UPS is rated 300kVA but never loaded beyond 50%. So one choice is to install a 300 kVA 480DY isolation transformer. This seems excessive? Could a zig-zag transformer be used upstream of the UPS input to derive a neutral?
The customer has some load that could be connected upstream using a 480Y:240D transformer. Would the Wye primary derive a neutral?
My understanding is that the UPS requires the grounded wye due to components on board that are rated and connected for line to ground voltage as well as during a discharge for safety reasons since the input contactor is opened on discharge.
Any tips, advice or experiences would be helpful.
Thanks!
Our Customer purchased a new UPS that requires the input source to be a 480VAC grounded WYE. After the new UPS was installed it was determined that the Utility source is a 480 Delta.
The UPS is rated 300kVA but never loaded beyond 50%. So one choice is to install a 300 kVA 480DY isolation transformer. This seems excessive? Could a zig-zag transformer be used upstream of the UPS input to derive a neutral?
The customer has some load that could be connected upstream using a 480Y:240D transformer. Would the Wye primary derive a neutral?
My understanding is that the UPS requires the grounded wye due to components on board that are rated and connected for line to ground voltage as well as during a discharge for safety reasons since the input contactor is opened on discharge.
Any tips, advice or experiences would be helpful.