UPS - Short circuit Current

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
397
My client's spec for UPS states the below,

"The UPS shall be able to sustain overloads as follows:
150% load for 1 minute
125% load for 10 minutes
110% load for 1 hour."

While the overloading at 125% for 10 minutes and 150% for 1 minute, could be achieved by the venodors, but 100% overloading for 1 hour could not achieved, so vendors offer the next higher rating or the oversized UPS.

This raises the question that why would some one specify the overloading at 100% for 1 hour? I heard that this is to increase the short circuit current from the UPS?

Why to increase the short circuit current from the UPS?
 
Replies continue below

Recommended for you

NickParker, what you wrote is 110% load for 1 hour and that corresponds to 10% overload (and not 100% overload). Isn't it!
10% overload for 1 hour is not abnormal.
Wonder why the vendor is proposing higher rated UPS?
 
It is not an abnormal specification, but yes it does usually result in de-rating (oversizing) the UPS.

As for short-circuit currents, this is a sticky issue that UPS normally normally requires to go into bypass to supply from the source to provide enough fault current to trip the downstream protection in a fault. In battery mode the UPS is often unable to supply enough fault current.

Every project I have worked on (not as the designer) has effectively ignored this issue.
 