Recently my company purchased equipment that used 115V, 1P, 60 Hz motors. However, the equipment application was for a 115V, 50 Hz power system. To address the reduced frequency, the supplier provided 277V, 1P, 50 Hz motors. Again, the available power is 120/208, 50 Hz.
Questions:
1. For the 277V motor, the volts to hertz ratio is as follows:
@ 60 Hz: 4.62
@ 50 Hz: 4.16 (i.e. ~10% decrease)
Everything I've read indicates the key is to maintain the volts per hertz ratio. Would this decrease be acceptable? What is an acceptable range for volts per hertz deviation?