Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Use of NEC Tap Rule

Status
Not open for further replies.

richanton

Electrical
Jul 15, 2002
128
I have a situation where I have an existing 100 amp 3 phase service out of a panelboard. I would like to split the service in a junction box by terminating on a power distribution block and then feeding 3 individual 2 pole 30 amp receptacles mounted in the side of the jbox. There are #1AWG conductors coming in and I want to make the taps with #8AWG wire.

The receptacles are used to feed computer rack PDU's. The cord has no main breaker, but has 6 overload breakers(1 for 2 PDU receptacles) to protect the load side.

Is this a proper application of the NEC 240-21 10 foot tap rule?
 
Replies continue below

Recommended for you

The answer to your question is NO. Read 240.21(B)(3), which states the the tap conductors must be enclosed in a raceway. You need 3 each 2 pole overcurrent devices before your receptacles.
Without knowing the voltage and is it delta or wye system. I would use interlocking switch fuse receptacle so that the load is switched off before removing the plug cap. Also is this computer a critical operations data system? If it is, see Art. 708, 700, and 645.
BTW the term you FEEDER, not service. Please, next post include all pertinent info.
Good luck!
 
After re-reading the code section several times, and finding some Mike Holt comments on the subject, it looks like you are correct. I do need that protective device before I go to any receptacle. Thanks for the input.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor