richanton
Electrical
- Jul 15, 2002
- 128
I have a situation where I have an existing 100 amp 3 phase service out of a panelboard. I would like to split the service in a junction box by terminating on a power distribution block and then feeding 3 individual 2 pole 30 amp receptacles mounted in the side of the jbox. There are #1AWG conductors coming in and I want to make the taps with #8AWG wire.
The receptacles are used to feed computer rack PDU's. The cord has no main breaker, but has 6 overload breakers(1 for 2 PDU receptacles) to protect the load side.
Is this a proper application of the NEC 240-21 10 foot tap rule?
The receptacles are used to feed computer rack PDU's. The cord has no main breaker, but has 6 overload breakers(1 for 2 PDU receptacles) to protect the load side.
Is this a proper application of the NEC 240-21 10 foot tap rule?