I have a 3-phase 208 volt emergency generator that I want to use for single phase loads. Is there any problem with running the generator for prolonged periods while only using two of the three legs?

---KenRad
 
Replies continue below

Recommended for you

Why not install a 120/208 3 phase panel and balance your single phase load on all phases?
 
If you have access to both ends of all three windings you can connect them so that you get 120/240 single phase using all three windings. /\._ Each line is one winding, the dot is the neutral.
 

wareagle has the best suggestion—it permits full-capacity-genset loading. If no 120V loads are served, you could also jack that puppy's AVR up to 139V/coil and get 240V ø-ø times three.

For connecting “edison 3-wire” service to a 12-lead stator, see page 6+ of www.marathonelectric.com/generators/BROCHURE/GPN016.pdf   In all three cases reduce available power to two-thirds of nameplate.

DOUBLE-DELTA—SINGLE-PHASE CONNECTION  Most typical arrangement.

LOW ZIG-ZAG—SINGLE-PHASE CONNECTION  {Also termed “Le Blanc”} Less voltage balance with respect to neutral, and the fun of making two sets of 4+ wire pigtail wads.

HIGH-VOLTAGE—SERIES-DELTA CONNECTION   {Abandon/tape off “L1” external connection} Fine for 120/240V 3-wire if full neutral current is not needed {<50%.} Makes easier pigtail bolting/taping.
 