majesus
Electrical
- Aug 16, 2007
- 262
I got an application where a Toshiba MV VFD powers a 6000ft Overland conveyor. There is a E-stop pull cord on one side of the conveyor, so I have about ~12000ft of E-stop wiring to deal with. So my intention is going with a DC system.
(The Toshiba VFD has an internal incoming contactor for E-stop function.)
Looking at Rockwell Automation's Safety Relay MSR5T, it operates at 24Vdc, it says the Maximum Input Resistance is 200ohms.
Trying to understand the meaning. Ignore all other factors and just deal with resistance in the circuit from only the cable run. Say I chose #10AWG, with a resistance of ~1.10ohm/1000ft. I can go about 181,000ft in wire length before I have an issue? That's 34 miles! What am I missing?
Cheers,
Majesus