- Jun 22, 2006
- 2
I have a well with a 2 HP single phase 240 volt submersible pump that needs to be replaced. The pump is 600 ft. down in the well. It has #8/3 cable feeding it now
I would like to replace it a 3 HP submersible pump. On a pump manufacturer's your web site they show the maximum depth for a 3 hp pump on #8 is 470 ft.
I have not been able to find the full load amps for the pump on to the pump manufacturer's web site so I used 17 amps from table 230.248 of the National Electrical Code for a 3 hp single phase motor for my calculations
The voltage drop for 17 amps motor load at 600 ft at 240v single phase is 15.4 volts exceeding the voltage drop of 3 percent allow for a branch circuit by the National Electrical Code and also 600 ft is deeper than a 3 hp pump will operate according to the pump manufacturer's web site
My question is can I use a buck and boost transformer ahead of the new controller to boost the voltage by 12 volts to 252 volts to operate the 3 hp pump on my existing #8 cable.
The pump motor is my main concern if controller components fail prematurely they can be easily replaced.
This is more of a technical question than a code question but input on both would be appreciated
Please excuse the long post
Thanks
I would like to replace it a 3 HP submersible pump. On a pump manufacturer's your web site they show the maximum depth for a 3 hp pump on #8 is 470 ft.
I have not been able to find the full load amps for the pump on to the pump manufacturer's web site so I used 17 amps from table 230.248 of the National Electrical Code for a 3 hp single phase motor for my calculations
The voltage drop for 17 amps motor load at 600 ft at 240v single phase is 15.4 volts exceeding the voltage drop of 3 percent allow for a branch circuit by the National Electrical Code and also 600 ft is deeper than a 3 hp pump will operate according to the pump manufacturer's web site
My question is can I use a buck and boost transformer ahead of the new controller to boost the voltage by 12 volts to 252 volts to operate the 3 hp pump on my existing #8 cable.
The pump motor is my main concern if controller components fail prematurely they can be easily replaced.
This is more of a technical question than a code question but input on both would be appreciated
Please excuse the long post
Thanks