nader666
Structural
- Mar 7, 2013
- 21
Hi everyone,
I am a reviewing a tank design calculation submitted by a NYS Structural Engineer.
I do not agree with the calculation and I want to get your opinion about some of the assumptions in the structural
calculation report.
1. The report considered ACI 350 just a recommendation and based on that ACI 318 has been used to eliminate the
sanitary factor (1.3) and reduce the design moment on the tank walls.
2. The calculation is based on PCA tables but it did not follow the listed modification in the book calculation.
3. The calculation used minimum area steel equations listed in ACI 350 (As, min = ((3 x square root(f’c))/fy) x bw x d
≥ (200/fy) x bw x d) and then claimed that even the horizontal reinforcement is not meeting those equations, it is ok
because ACI 350 is only recommendation and the horizontal rebars area steel satisfies the minimum temperature &
shrinkage area steel listed in ACI 318!, As far as I know, the minimum area steel equation listed in ACI 350 is
adopted and listed in ACI 318 should be applied using both code. The horizontal reinforcement of the walls is
# 4 @ 12" .
I would appreciate your opinion.
Thank You
Nader Soliman, P.E.
I am a reviewing a tank design calculation submitted by a NYS Structural Engineer.
I do not agree with the calculation and I want to get your opinion about some of the assumptions in the structural
calculation report.
1. The report considered ACI 350 just a recommendation and based on that ACI 318 has been used to eliminate the
sanitary factor (1.3) and reduce the design moment on the tank walls.
2. The calculation is based on PCA tables but it did not follow the listed modification in the book calculation.
3. The calculation used minimum area steel equations listed in ACI 350 (As, min = ((3 x square root(f’c))/fy) x bw x d
≥ (200/fy) x bw x d) and then claimed that even the horizontal reinforcement is not meeting those equations, it is ok
because ACI 350 is only recommendation and the horizontal rebars area steel satisfies the minimum temperature &
shrinkage area steel listed in ACI 318!, As far as I know, the minimum area steel equation listed in ACI 350 is
adopted and listed in ACI 318 should be applied using both code. The horizontal reinforcement of the walls is
# 4 @ 12" .
I would appreciate your opinion.
Thank You
Nader Soliman, P.E.