We are working on a project where a new 3000A swtichboard is being installed at an industrial facility, but the customer wants to use the existing conductors and rigid steel conduit for the feeders to all of the loads. None of them have equipment grounding conductors (EGC's) installed. While using the conduit as an EGC is legal per code, in almost all of our installations we do not do it; however, in this instance it might be necessary.
We can't find any sizing requirements for the conduit to be used in this way. NEC 250.122 does not give a specific size for the conduit based off of the breaker ampacity. Does such a table exist that we are missing, or is there an industry standard that's out there?
We can't find any sizing requirements for the conduit to be used in this way. NEC 250.122 does not give a specific size for the conduit based off of the breaker ampacity. Does such a table exist that we are missing, or is there an industry standard that's out there?