I recently used a 4" thick s.o.g. to laterally brace the bottom of a cast-in-place concrete foundation wall. The s.o.g. only has wwf reinforcment for crack control in it. The foundation wall retains about 14' of earth, and was designed per the geotech engrs recommendations for an "at rest" earth pressure. The lateral force at the bottom of the wall due to the earth pressure is quite large (about 3.8 k/ft), due to the height of retained backfill.
Dead loads on the wall and footing ( including wall self-weight and earth above the projecting edge of the footing) are not enough to provide enough frictional resistance to counteract this lateral force (Let alone provide a safety factor against sliding). The frictional sliding resistance is only about 1.7 k/ft. The footing would need to get pretty big to catch enough backfill dead load to make any difference.
Basement walls in this building oppose each other in plan, so I used the slab-on-grade as a horizontal diaphragm, with the forces at the bottoms of the walls canceling each other.
The basement s.o.g. will be sawcut about 3/4" to provide relief of shrinkage stresses. That leaves about 3 1/4" thickness of slab as effectve. The compressive stress in the concrete may reach 55 psi +-. That didn't seem like much when I first checked this, but now I wonder. It may be possible that the lateral force going into the slab will load the concrete eccentrically, perhaps buckling it upwards, or otherwise damaging it. (Although, in many buildings I've worked on in the past with a similar detail, this has never been a problem.)
I have not thought about this concern much before but now I have revisited the design and wonder if my assumptions were correct.
Do any of you have any experience or comments on this condition?
Any comments greatly appreciated. Please help me sleep.
Dead loads on the wall and footing ( including wall self-weight and earth above the projecting edge of the footing) are not enough to provide enough frictional resistance to counteract this lateral force (Let alone provide a safety factor against sliding). The frictional sliding resistance is only about 1.7 k/ft. The footing would need to get pretty big to catch enough backfill dead load to make any difference.
Basement walls in this building oppose each other in plan, so I used the slab-on-grade as a horizontal diaphragm, with the forces at the bottoms of the walls canceling each other.
The basement s.o.g. will be sawcut about 3/4" to provide relief of shrinkage stresses. That leaves about 3 1/4" thickness of slab as effectve. The compressive stress in the concrete may reach 55 psi +-. That didn't seem like much when I first checked this, but now I wonder. It may be possible that the lateral force going into the slab will load the concrete eccentrically, perhaps buckling it upwards, or otherwise damaging it. (Although, in many buildings I've worked on in the past with a similar detail, this has never been a problem.)
I have not thought about this concern much before but now I have revisited the design and wonder if my assumptions were correct.
Do any of you have any experience or comments on this condition?
Any comments greatly appreciated. Please help me sleep.