Gentlemen,
An AE firm came up with the settings for a Siemens WL breaker with an ETU trip unit. I think they used SKM software to get the numbers.
This involves a recently installed Goulds reclaim water pump driven by a Reliance 460 V, 250 hp motor. FLA=272A. LRA=1825A.
Trip Unit Settings:
Rating plug = 300A
Long Time Pickup = 1
Long Time Delay = 8s @ 6 x PU
Short Time Pickup = 8
Short Time Delay = 0.02s (fixed)
Instantaneous = 12
I think I understand the purpose of short time protection to achieve coordination between feeder breakers and upstream breakers. My question concerns the application of short time protection for a motor circuit.
What do you think it is there for?
An AE firm came up with the settings for a Siemens WL breaker with an ETU trip unit. I think they used SKM software to get the numbers.
This involves a recently installed Goulds reclaim water pump driven by a Reliance 460 V, 250 hp motor. FLA=272A. LRA=1825A.
Trip Unit Settings:
Rating plug = 300A
Long Time Pickup = 1
Long Time Delay = 8s @ 6 x PU
Short Time Pickup = 8
Short Time Delay = 0.02s (fixed)
Instantaneous = 12
I think I understand the purpose of short time protection to achieve coordination between feeder breakers and upstream breakers. My question concerns the application of short time protection for a motor circuit.
What do you think it is there for?