rockman7892
Electrical
- Apr 7, 2008
- 1,161
I'm looking at a project that has a distribution bus on the secondary of a 13.2kV delta transformer which (wye primary winding has to do with generator and grid connections) has a zig-zag transformer specified to be connected to the distribution bus to provide a ground fault sources on the delta system. The specified zig-zag transformer is specified to be a 3.2MVA transformer with a grounding resistor connected to the neutral.
It is proving difficult to find such a transformer however I believe that a standard wye-delta transformer can be connected with the wye side connected to the system bus in order to achieve the same result? From what I have read it seems to be that these wye-delta grounding transformers are typically single-phase transformers connected together for a 3-phase transformer? Can a standard 3-Phase distribution type transformer be used to provide this grounding source?
From what I've seen the kVA rating of the transformer is typically sized in order to support the ground fault current that will be dictated by the resistor size. After calculating the transformer size based on fault current you can then apply multiplier to kVA rating based on C57.92-06.200 for clearing faults in a specified period of time (in order to reduce kVA size).
Is this as straight forward as calculating a standard 3-Phase distribution transformer size or are there certain reasons why the ZZ transformer is a better choice?
I cant seem to find what the specified resistor size was for zig-zag transformer but am assuming it is intended to be a LRG system (I'm getting more info)
It is proving difficult to find such a transformer however I believe that a standard wye-delta transformer can be connected with the wye side connected to the system bus in order to achieve the same result? From what I have read it seems to be that these wye-delta grounding transformers are typically single-phase transformers connected together for a 3-phase transformer? Can a standard 3-Phase distribution type transformer be used to provide this grounding source?
From what I've seen the kVA rating of the transformer is typically sized in order to support the ground fault current that will be dictated by the resistor size. After calculating the transformer size based on fault current you can then apply multiplier to kVA rating based on C57.92-06.200 for clearing faults in a specified period of time (in order to reduce kVA size).
Is this as straight forward as calculating a standard 3-Phase distribution transformer size or are there certain reasons why the ZZ transformer is a better choice?
I cant seem to find what the specified resistor size was for zig-zag transformer but am assuming it is intended to be a LRG system (I'm getting more info)