rockman7892
Electrical
- Apr 7, 2008
- 1,161
Are there any issues with using 50/5 zero sequence CT's for ground fault protection of a solidly grounded 4.16kV system? I thought I had heard once that there could be a potential saturation issue with using this CT on a solidly grounded system with lots of ground fault current available?
I know a residual connection will work fine on a solidly grounded system and zero sequence CT's are typically reserved for resistance grounded systems with minimal fault current however I'm looking at a particular situation where zero sequence CT's are already existing in a solidly grounded system.
If there are no issues with using these CT's is there a rule of thumb for setting these on transformer feeder circuits? I believe I have seen a reference which recommended setting the relay for an INST pickup of 10A with a 20-30ms delay when using zero sequence? With residual CT's on transformer circuit I've always used minimum tap setting with INST set to 4x transformer FLA as 0.2 sec.
I know a residual connection will work fine on a solidly grounded system and zero sequence CT's are typically reserved for resistance grounded systems with minimal fault current however I'm looking at a particular situation where zero sequence CT's are already existing in a solidly grounded system.
If there are no issues with using these CT's is there a rule of thumb for setting these on transformer feeder circuits? I believe I have seen a reference which recommended setting the relay for an INST pickup of 10A with a 20-30ms delay when using zero sequence? With residual CT's on transformer circuit I've always used minimum tap setting with INST set to 4x transformer FLA as 0.2 sec.