In SKM software, the Utility contribution is modeled considering the nominal voltage delivered by the Utility and a Thevinin Impedance.
For load flow calculations, SKM has an option to include or not to include this impedance.
If we include it, the voltage drop from this Utility Thevenin Impedance could be substantial, (I.e. 2% to 3.5% or so).
Add to this voltage drop, the voltage drop of the transformer and we start with a high voltage drop (from the nominal secondary voltage) at the secondary of the service transformer.
Due to this fact, I do not include the transformer impedance in my low flow calculations.
Do you include it? If you do, why?
I have a customer that insists that the Utility impedance should be included but gives little explanation why.
For load flow calculations, SKM has an option to include or not to include this impedance.
If we include it, the voltage drop from this Utility Thevenin Impedance could be substantial, (I.e. 2% to 3.5% or so).
Add to this voltage drop, the voltage drop of the transformer and we start with a high voltage drop (from the nominal secondary voltage) at the secondary of the service transformer.
Due to this fact, I do not include the transformer impedance in my low flow calculations.
Do you include it? If you do, why?
I have a customer that insists that the Utility impedance should be included but gives little explanation why.