ladengr
Electrical
- Jun 12, 2004
- 20
How do you interpret the following electrical installation?
1. 2000 Amps, 480/277 Volts Main service is grounded as per NEC 250B(2). Service has a GFP.
2. Four wire Generator neutral is bonded and grounded. Generator has two CBs and rated 400 Amps and has no GFP. 3 pole and 4 pole transfer switches are installed. 3 pole ATS serves a 3 phase motor load and no neutral wire is required. 4pole transfer switch serves 277 volts and 480 Volts loads.
Does this installation comply with NEC Article 250 - 20?
1. 2000 Amps, 480/277 Volts Main service is grounded as per NEC 250B(2). Service has a GFP.
2. Four wire Generator neutral is bonded and grounded. Generator has two CBs and rated 400 Amps and has no GFP. 3 pole and 4 pole transfer switches are installed. 3 pole ATS serves a 3 phase motor load and no neutral wire is required. 4pole transfer switch serves 277 volts and 480 Volts loads.
Does this installation comply with NEC Article 250 - 20?