un421ate1
Electrical
- Apr 12, 2003
- 21
The local utility requires two indicating lights on the front of their 13Kv switchgear to indicate the position of a generator air-circuit breaker installed downstream that operates in parallel with the utility.
Because of a shortage of auxilliary contacts on the generator air circuit breaker I used the one available "A"
contact to energize a relay and used its n/o, n/c contacts
to power the indicating lights (red closed..green open).
The engineer said this arrangement violated ANSI standards
and that the lights must be powered through mechanically linked generator breaker contacts..
Is he correct and if so what's the relevant code requirement.
many thanks.