I am having trouble satisfying outside air requiremetns with VVT (VAV-bypass)system. Here is an example
Class room 500 sq. ft
Students: 25
OA required = 25x15 = 375
HVAC Unit = 20-ton with 40% OA (8000 cfm total air, 3200 cfm OA)
Summer Operation:
Supply Air = 1000 (vav box fully open)
OA supplied to the class = 1000*40% = 400
OA requriements are met? YES
Winter Operation:
Box closes 50%
Supply air = 500 cfm
Outside air supplied = 500*40% = 200 cfm
OA requirements met? NO
If it was true VAV system, my outside air would be 80% on the unit, and will satisfy room OA requirements. But
this is V V T system, which has constant air flow with by-pass damper. So, we have constant flow of 8000 cfm and 3200 cfm OA at the unit.
Sincerely,
Fayaz Din
Class room 500 sq. ft
Students: 25
OA required = 25x15 = 375
HVAC Unit = 20-ton with 40% OA (8000 cfm total air, 3200 cfm OA)
Summer Operation:
Supply Air = 1000 (vav box fully open)
OA supplied to the class = 1000*40% = 400
OA requriements are met? YES
Winter Operation:
Box closes 50%
Supply air = 500 cfm
Outside air supplied = 500*40% = 200 cfm
OA requirements met? NO
If it was true VAV system, my outside air would be 80% on the unit, and will satisfy room OA requirements. But
this is V V T system, which has constant air flow with by-pass damper. So, we have constant flow of 8000 cfm and 3200 cfm OA at the unit.
Sincerely,
Fayaz Din