There are two vista switchgears, one fed from A-side and the other one fed from B-side. These switchgears serves transformers.
Since the B vista switchgear is energized through the closed loop switch in each transformer a fault on a primary conductor will be fed direct from the utility and also through the primaries feeding the other transformers. The loop feed switch at the transformers creates a direct connection between the A and B side primary conductors without going through the transformer.
The VFI feeding the faulted line and the A side should open first and the B side VFI should also open since it will be back fed through the other transformer primary conductors. Currently both the VFIs are set as
Pick up - 200A
U2 Inverse - 0.5
Instantaneous - 1000
Definite time - 96ms
If I bring down the definite time setting of the A-side VFI to 80ms,will this solve the issue?
Thanks
Since the B vista switchgear is energized through the closed loop switch in each transformer a fault on a primary conductor will be fed direct from the utility and also through the primaries feeding the other transformers. The loop feed switch at the transformers creates a direct connection between the A and B side primary conductors without going through the transformer.