Vacuum Testing a Wet Well

Status
Not open for further replies.

Joncrete

Civil/Environmental
Jan 7, 2010
5
0
0
US
How can a large Wet Well (10' or 12') be Vacuum tested if the Access Hatch is not Air Tight?

And also other holes in the Top Slab such as holes for Electrical/Floats which can be difficult to plug.
 
Replies continue below

Recommended for you

Mechanically anchor a liner over the access hatch and seal with elastomeric sealant.

Use watertight pipe/electrical connections with gasketed pipe bell connectors or sleeves for boot type connectors.
 