Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Valve body and correlation with Cv

Status
Not open for further replies.

johcatrac

Mechanical
May 3, 2008
43
A valve vendor is claiming that there is little correlation between the valve body inside contours and the Cv. The valve in question is a globe valve. My instinct says this is incorrect, however would appreciate any expert or experienced insight.
 
Replies continue below

Recommended for you

Flow contours really only come into play when you are near full-open, high flow rates. Are you planning to use the valve as a control element in such conditions?
 
Yes, the valve is a control valve in mid to fully open range.
 
I don't fully understand their statement, since a more tortuous path will lead to increased losses/less flow, but maybe they're talking in generalities that "x" type of contour doesn't necessarily correlate to higher flow?

If they have open percentage vs Cv I would just go with that unless you have concerns?
 