I have been asked to troubleshoot an LPG system. There are 4 racks of 7' dia. bullets, 5 bullets to a rack. The five bullets in a rack feed a booster pump at a rate of 600 gpm with a 4" line from each bullet. On hot days, above 70 F with the sun out, the pumps vapor-lock. When the bullets drop below 3' they vapor-lock. A hysys model of the system shows that at a starting pressure of 135 psig the highest temperature that can be tolerated is 80 F. Once the bullets drop to 3' at a pressure of 104 psig, the highest temperature that can be tolerated is 63 F.
Operations installed a line off the suction line of the pump that goes to flare. This helps de-gas the pipe. Is there a better way to avoid this problem.
I've suggested re-circulating some of the flow back to the bullets from the discharge of the pump. That is, moving the line from the suction to the discharge. Instead, others are pursuing changes to the control valve.