Hey everyone, I'm hoping someone here will be able to give me some input.
I'm trying to troubleshoot some issues we have been having with one of our units. The primary issue is that the governor system, Vevey Type 200, will intermittantly slam the gates closed while running online. It appears as though there is either an input that is failing intermittantly, causing the governor to drive the gates closed, or one of the control paths in the governor itself is failing, causing the gates to slam closed. I've experienced a similar problem here, when a different unit was being placed on Joint Load control, the load setting signal was being grounded out, telling the governor to immediately go to 0% load. We are monitoring a number of points with an event recorder to determine the actual point of failure. However, here's where I need some help.
Looking at the data captured on our UCMS system, we see that the gates swing closed, followed immediately by a significant increase in field voltage, field current, and VARs. The actual event looks like this. The gates drop from approx 80% to approx 40%. Then the gates swing back up to about 60%, then down to full close, back up to about 15%, back to full close, up to about 30%, full close, then start climbing back to normal gate position. The speed at which these swings occur seem to be limited only by the actual gate timing itself. When this happens, every time the gates swing closed, the unit's VARs swing up. When the gates swing open, VARs swing down. The VAR swing is approximately 40-50 MVARS, peak to peak.
I understand rapid gate movement will cause the REAL power (watts) to surge like this, but I can't understand if these VAR swings are a natural consequence of gate swing. If it is, then the problem should be resolved when we fix the governor issue. I'm just not sure if that's the case, or if we are looking at bigger problems that a intermittant fault on the governor system.
Could someone please tell me if VARS should swing with rapid gate movement?
Thank you very much in advance.
I'm trying to troubleshoot some issues we have been having with one of our units. The primary issue is that the governor system, Vevey Type 200, will intermittantly slam the gates closed while running online. It appears as though there is either an input that is failing intermittantly, causing the governor to drive the gates closed, or one of the control paths in the governor itself is failing, causing the gates to slam closed. I've experienced a similar problem here, when a different unit was being placed on Joint Load control, the load setting signal was being grounded out, telling the governor to immediately go to 0% load. We are monitoring a number of points with an event recorder to determine the actual point of failure. However, here's where I need some help.
Looking at the data captured on our UCMS system, we see that the gates swing closed, followed immediately by a significant increase in field voltage, field current, and VARs. The actual event looks like this. The gates drop from approx 80% to approx 40%. Then the gates swing back up to about 60%, then down to full close, back up to about 15%, back to full close, up to about 30%, full close, then start climbing back to normal gate position. The speed at which these swings occur seem to be limited only by the actual gate timing itself. When this happens, every time the gates swing closed, the unit's VARs swing up. When the gates swing open, VARs swing down. The VAR swing is approximately 40-50 MVARS, peak to peak.
I understand rapid gate movement will cause the REAL power (watts) to surge like this, but I can't understand if these VAR swings are a natural consequence of gate swing. If it is, then the problem should be resolved when we fix the governor issue. I'm just not sure if that's the case, or if we are looking at bigger problems that a intermittant fault on the governor system.
Could someone please tell me if VARS should swing with rapid gate movement?
Thank you very much in advance.