EddyWirbelstrom

Electrical
Feb 17, 2002
216
ABB variable speed drives type ACS580 with front-end uncontrolled 6 pulse rectifier are supplied via Delta-Wye Ground transformers.
The ABB DriveSize Ver 5.9 software reports triplen and even order harmonic currents injected into the system impedance, on both sides of the Delta-Wye Ground transformer.
How can triplen and even order harmonic currents flow in the system imepdance ?

 
Replies continue below

Recommended for you

My earlier post incorrectly stated that the ABB DriveSize 5.9 reported triplen and even harmonics.
The attached DriveSize 5.9 report for a 315kW VSD shows insignificant triplen and even harmonics.
 
 https://files.engineering.com/getfile.aspx?folder=a32055a9-659d-4063-a06d-207b820ac277&file=ACS580-07-585-4_315-315kW_no_Triplen+Even.xlsx