Corect me if Im wrong? (by the way im in Germany)
Typical VAV system.
Max. box position - full cooling
Min. box position - minimum cooling
The VAV modulated between both max & min position. Min position ensures min air change rates and grille air diffusion index is achieved
When heating is required at min position the box reheat coil modulated from 0-100% open to achieve room temperature.This is all stock standard.
Q. The designer now wants if the room is still not satisified when in heating mode, to open up the box again from min up towards max. ( the grilles are over sized and velocity at min. is too low and the hot air is stagnant at the ceiling) Looks like this is her get out solution to grille problem, but its a waste of energy as far as I can see having the main AHU speed drive ramping up when in heating
Is this crazy , especially on internal zone boxes, in the middle of Spring. I could understand perimeter zone in really cold environments with poor perimeter glazing & insulation, so your supply air temp is not too hot (above 30deg) ramp up then. What do you think???
Typical VAV system.
Max. box position - full cooling
Min. box position - minimum cooling
The VAV modulated between both max & min position. Min position ensures min air change rates and grille air diffusion index is achieved
When heating is required at min position the box reheat coil modulated from 0-100% open to achieve room temperature.This is all stock standard.
Q. The designer now wants if the room is still not satisified when in heating mode, to open up the box again from min up towards max. ( the grilles are over sized and velocity at min. is too low and the hot air is stagnant at the ceiling) Looks like this is her get out solution to grille problem, but its a waste of energy as far as I can see having the main AHU speed drive ramping up when in heating
Is this crazy , especially on internal zone boxes, in the middle of Spring. I could understand perimeter zone in really cold environments with poor perimeter glazing & insulation, so your supply air temp is not too hot (above 30deg) ramp up then. What do you think???